winslowfam
Senior Member
- Location
- VA
Hi...our client has a new PV system with 2 inverters, whose outputs are connected to a new PV System Disc. Sw., and then to an isolation transformer. The transformer is wired 480/277V WYE primary/480V DELTA secondary, with the secondary is wired to a new overall system AC Disc. Sw. This switch is then wired to the existing plant power system. Proper grounding and bonding was designed all the way through to the transformer, per code. But, the transformer secondary (DELTA - so, no neutral) was not bonded to the new AC Disc. Sw. This new switch, though, is bonded to the plant system ground via an EGC. So, the overall PV system is grounded WYE to the transformer primary, then ungrounded 480V from transformer secondary to the AC Disc. Sw., but then is back to a grounded 480V from the AC Disc. Sw. to where it connects to the plant system. Is this correct? Shouldn't the transformer secondary be bonded to the plant ground system somehow instead of being ungrounded?