hbendillo
Senior Member
- Location
- South carolina
I am wondering if there is ever a condition where the load side of an automatic transfer switch (ATS) would require overcurrent protection if both the normal and emergency feeders both have overcurrent protection. This is not an service rated ATS question but typical condition. I.E. feeder with OCP from building normal power switchboard feeds normal side of ATS and Generator with main feeder breaker feeds emergency side of ATS . The load side of ATS feeds a panelboard adjacent to the ATS. I always show a main breaker in the emergency panelboard.
The design issue I am considering: Feeding an existing emergency section of a switchboard from a new ATS. New ATS fed from generator with integral circuit breaker for the emergency feed, new ATS fed from breaker in normal power switchboard on normal side, load side of ATS feeds the emergency section that has no main circuit breaker. The new ATS is in same room as the load but not right next to it Probably 10 feet away on an adjacent wall. Is any additional overcurrent protection required on the load side of the ATS?
Next issue: Owner is worried about space to install the ATS the same room as the load. Wants us to locate the ATS in an adjacent room not in sight of the load. Does this present any issues?
The design issue I am considering: Feeding an existing emergency section of a switchboard from a new ATS. New ATS fed from generator with integral circuit breaker for the emergency feed, new ATS fed from breaker in normal power switchboard on normal side, load side of ATS feeds the emergency section that has no main circuit breaker. The new ATS is in same room as the load but not right next to it Probably 10 feet away on an adjacent wall. Is any additional overcurrent protection required on the load side of the ATS?
Next issue: Owner is worried about space to install the ATS the same room as the load. Wants us to locate the ATS in an adjacent room not in sight of the load. Does this present any issues?