Alb
- West Chicago, ILL, DuPage County
My panel is maxed out, and I need to install an 240V-50Amp outlet for an electric range. Licensed electrician suggested replacing an existing 30Amp double pole breaker for the garage with the 50Amp breaker, then double tap from the same breaker to feed both the 50amp range, and the garage.
I told him this is a violation; that each conductor must terminate in an individual terminal within the panelboard.( NEC 408.41).
He said it's no big deal, it's common practice, everybody does it. He is a licensed, insured, bonded electrician.
Any thoughts on this? Thank you.