I have a new service with a new Siemens meter stack, that includes a 400 amp meter. (I think its actually a class 320 meter). The available short circuit current at the meter stack is 35KAIC.
The meter has a 65K rated breaker on the line side of the meter, but the shop drawings indicate the meter only has a 25 KAIC rating.
I asked the rep why the rating on the meter is lower than the breaker rating, and the engineer he asked said its because the breaker has a let through current of more than 30K.
The rep. also said all their 400 amp meter bases have the same 25KAIC limit.
Questions:
1. Surely people put 400 amp meters on systems with more than 25K available all the time. Is this a compliant install? I would think not.
2. If its not compliant, how can I make it so? Would installing a current limiting fuse make this code compliant?
Common sense tells me this isn't a safe installation, but I also have a feeling there must be installs like this going in every single day.
The meter has a 65K rated breaker on the line side of the meter, but the shop drawings indicate the meter only has a 25 KAIC rating.
I asked the rep why the rating on the meter is lower than the breaker rating, and the engineer he asked said its because the breaker has a let through current of more than 30K.
The rep. also said all their 400 amp meter bases have the same 25KAIC limit.
Questions:
1. Surely people put 400 amp meters on systems with more than 25K available all the time. Is this a compliant install? I would think not.
2. If its not compliant, how can I make it so? Would installing a current limiting fuse make this code compliant?
Common sense tells me this isn't a safe installation, but I also have a feeling there must be installs like this going in every single day.