Panel feeders
A customer asked us to give an alternative price for running his 3 phase 120/208 feeder conductors in aluminum. Feeders are coming out of a 200 amp breaker on a gangable meter compartment to a 225 amp main lug panel. Are we able to use 4/0 aluminum XHHW if the lugs are rated for 90 degree? are we allowed to round up to the next over current device?
You must use the 75 degree column as your equipment will be rated for 75 degree max termination. You could, however, use the next size up rule the 4/0 AL would be OK IF the calculated load does not exceed 180 amps. Thats a big if in many AHJs eyes, especially if you don't have the data to back it up.
I agree with Texie. I'd bring your load calc sheet with you for inspection if you go with the 4/0, just in case.
Thanks. Was hoping to find some cost savings with Al conductors but will not be very effective if I have to go up to #250 MCM.
Wouldn't the larger size aluminum conductors still be about 1/2 the cost of smaller copper conductors?