Fulthrotl
~Autocorrect is My Worst Enema.~
- E
here's my problem...... as i see it anyway....
i have a fluke megger. works fine on reasonable runs.....
say, 4/0 a few hundred feet long......
i have to megger three sets of 750 mcm copper thwn,
in parallel, that are 750' long... so that's 2,100' per
leg, and my little meter just won't pull it.
so, i need to go get a "real" megger that i can put
1kv on this beast, and see where the insulation value
is at.
the readings i'm getting, are not good, and i suspect
the dielectric load is exceeding the little fluke's ability
to perform.
what megger should i go looking to rent?
is at.
to perform.