sparkycoog
Member
- Location
- Texas
Sorry to be vague, but after having some issues with 20 amp fuses on a dimming system burning out and contacting the manufacturer (which will remain anonymous as will I) they limit their 20 amp line side to 8.3 amps for magnetic low voltage loads (such as MR-16 fixtures, transformers for low voltage lights, etc). The same system can handle the full 16 amps of a continuous load for incandescent loads. This was news to me. I always thought that it would just be 80% of the 16 amps and the maximum is 12.6 amps (and I had gone even below that) and it still blew out the fuse. They now have the 8.3 amps written in the documentation but it wasn't there before when this system was installed so when I asked about it, I was told that this was always in the NEC and it hasn't changed regardless of the label.
Can someone please let me know where the 8.3 amps came from? Is this actually general knowledge NEC code that I was not aware of? I have to say, I feel rather stupid at the moment.
Can someone please let me know where the 8.3 amps came from? Is this actually general knowledge NEC code that I was not aware of? I have to say, I feel rather stupid at the moment.