In a retail facility, client has a food service counter for selling pizza by the slice, sandwiches, espresso, etc. Per NEC 210.8 it is a "kitchen", so all 20A receptacles are gfci, including the outlets at the Point of Sale.
Client intends to plug in a power-strip style point-of-use UPS so the computer has uninterrupted power.

The concern: EMI filters in the UPS may leak enough current to ground that it trips out the GFCI. If that happens, or if the GFCI trips out for another ground fault event, the UPS will immediately re-introduce 120V current back into the system.
I find nothing in the NEC addressing this. It seems problematic, but is it a violation of a code? Engineers can design a code-compliant system, but cannot control what end users plug into outlets.