I would like to perform a DC withstand test on equipment that will have electronic components without any open contacts in line with the component.  For example, I have SSRs and solenoids inside the equipment, but contacts that make/break these components are normally open.  These components normally remain off after the on/off switch to the equipment is switched to the on position.  Further logic has to be satisfied before the components become energized.
Also on the equipment are limit controllers, PID controllers, an HMI, PLC and a power supply--- these components all normally become energized as soon as the equipment on/off switch is moved to the on position. This means that when I perform the Insulation Resistance and then the Withstand test on the equipment, these components will definitely have the voltage at their input terminals. Granted, the line and neutral feeding the components are shorted together for the testing, so there will not actually be any voltage difference between the line and neutral inputs on the components.
Is it normal to do withstand tests on this type of equipment? I will unplug the equipment and short the line and neutral together on my power cord. I will then apply the test voltage between the shorted line and neutral terminals and the equipment grounding conductor. Should I be concerned about the components that will actually have this voltage connected directly to their input terminals?