I have a 10 HP compressor that im hooking up. Its recommended to be o a 200 amp fast acting fussed disconnect. This is 480 3phase. Its piped in 2inch EMT from panel to disconnect. Piped out of disconnect and changes over to a 10 foot section of sealtite. 3/0 THHN. Now here is the question. Im getting 3 different answers on the size of the equipment ground. The sales company and their field tech say #8 because the compressor wires are oversized and should be 2/0. The manufacturer has a sticker that says to use #2! And the NEC 250-122 says a number 6 is all I need. Im not going with the sales tech, but why would the manufacturer recommend a number 2? Is there something Im missing?