I think he meant that comment about all MCC units being removable as a joke (good one by the way, I'll have to use that). What you are describing would fall just outside of his "some are easier than others" category.Ok....maybe I have had experience with the ONLY non-removable buckets in existence. Several of our older pump stations have the main breaker hard-wired to the vertical bus behind the bucket. No way to remove it except de-energizing the MCC. Many are not in buckets at all, but are control cabinets with a fused disconnect in the same enclosure as the controls. Built in the 50's and 60's. As I stated before, troubleshooting a control circuit is often impossible unless the control is energized. Most are located in the same bucket as the 480 starters. Working in the now required PPE while doing so is EXTREMELY difficult, especially when using small tools or test leads. We do the best we can, but sometimes reality gets in the way. No more arguments from me, though. We all should know the rules and follow them. Nuff said.
Side story related to "some are easier than others".
I once did a project with an MCC lineup of 5kV 1000HP soft starters in 3 different pump stations. The specs called for providing two empty bays in the lineup for the "future addition of new soft starters". I put them on the end of the lineup, knowing full well what when the time came in the future, new starters would come in new structures, there is no such thing as an "open style" MV soft starter that can be mounted in the field into an existing box, because the main bus had to be removed and there would be too much liability for cable routing etc. on listed MV gear. The consultant, in his infinite wisdom, decided that he wanted the feeder switches on the end, so he made me change the "future unit" locations to the middle of the lineup. I warned him of the problem, he didn't seem to care. Flash forward 6 years, they finally released a contract to add those two new starters in each station. I work for a different company now and ours would not fit in that box, but I bid it anyway, figuring on adding them to the end with a transition section and moving the feeders in to the middle, re-pulling new conductors, running new conduits etc., the only way it COULD be done. I was way too high of course, but the poor guy that got the contract found out AFTER the fact that he could not do it the way the consultant had described it. They would NOT give him a change order, they said it was his responsibility to have understood the details. I hear he lost his ass on that contract.