According to NEC 450, if my transformer secondary current is less than 9A, if I size an OCPD at 1.67 times or less the secondary current, then I can protect my primary size at 250% the primary current. Or I can use 250% for the primary if the secondary amps are below 9A, and protected with 125% rounded up. I'm having trouble with making sense of how to calculate the secondary fuse size on a transformer that has a center tapped secondary.
My transformer is 2KVA. My secondary is 110 and 220V. If received some help on this forum about this, and began taking the 2KVA divided by the 220V, and then multiplying that by 1.25 to get my max secondary OCPD size. Is this correct? I can get a lot more current out of my transformer using the center tap, then going across the entire secondary.
My problem is that I want to find 1 circuit breaker size on my primary that will work between 380V and 480V (it is a multi tap primary, always 110-220 secondary). For 480V, using the 1.67 times I get a 7A circuit breaker (6.95 actually always so close on these calculations). For 380V using 1.67 I get an 8A breaker. I don't want to drive myself too crazy over a single Amp, but I do not want to have nuisance trips in the field by rounding down to the 7A breaker. I also want to be in accordance with the NEC and not size the primary too large (even if by 1 amp).
My secondary has a 10A circuit breaker between the secondary line and center tap (110V) and a 6A circuit breaker on a motor that is connected across the 220V of the secondary. The 1.67 times calculation on the secondary gives me a maximum of 15A combined OCPD's on the secondary to be able to size the primary up to 250% of the primary current. I'm one amp over here as well.
Am I adding the OCPD's on the secondary correctly? Should I only count the OCPD's across the entire secondary, or do I have to count the center tap as well? If so, then do am I limited to the amps across the entire secondary in my max OCPD sizing for the secondary?
My options are to either go with the 7Amp breaker and hope that it holds up well at 380V, or go with an 8Amp breaker and try to decrease my secondary OCPD's. The problem is that the particular UL489 breakers I am using goes 8A, 10A, 13A....no 9A. If I could use a 9A breaker I would have 15A total on the secondary and could size the primary larger. These are D-Curve breakers, would this hold up on a 2KVA general purpose transformer at 380V, in a 7A rating?
My transformer is 2KVA. My secondary is 110 and 220V. If received some help on this forum about this, and began taking the 2KVA divided by the 220V, and then multiplying that by 1.25 to get my max secondary OCPD size. Is this correct? I can get a lot more current out of my transformer using the center tap, then going across the entire secondary.
My problem is that I want to find 1 circuit breaker size on my primary that will work between 380V and 480V (it is a multi tap primary, always 110-220 secondary). For 480V, using the 1.67 times I get a 7A circuit breaker (6.95 actually always so close on these calculations). For 380V using 1.67 I get an 8A breaker. I don't want to drive myself too crazy over a single Amp, but I do not want to have nuisance trips in the field by rounding down to the 7A breaker. I also want to be in accordance with the NEC and not size the primary too large (even if by 1 amp).
My secondary has a 10A circuit breaker between the secondary line and center tap (110V) and a 6A circuit breaker on a motor that is connected across the 220V of the secondary. The 1.67 times calculation on the secondary gives me a maximum of 15A combined OCPD's on the secondary to be able to size the primary up to 250% of the primary current. I'm one amp over here as well.
Am I adding the OCPD's on the secondary correctly? Should I only count the OCPD's across the entire secondary, or do I have to count the center tap as well? If so, then do am I limited to the amps across the entire secondary in my max OCPD sizing for the secondary?
My options are to either go with the 7Amp breaker and hope that it holds up well at 380V, or go with an 8Amp breaker and try to decrease my secondary OCPD's. The problem is that the particular UL489 breakers I am using goes 8A, 10A, 13A....no 9A. If I could use a 9A breaker I would have 15A total on the secondary and could size the primary larger. These are D-Curve breakers, would this hold up on a 2KVA general purpose transformer at 380V, in a 7A rating?