Hello, sure would appreciate help with determining service conductors required considering adjustments per table 310.15. Or if another solution would be recommended.
The project is multifamily. Service load was calculated using 220.84. Load is 1276A with service voltage 240/120V single phase. The meter pack will have a 1400A breaker. The site also has 2 existing 4" schedule 80 pvc conduits. Ideally the 2 existing 4" conduits would be reused and not require trenching. Poco will not allow larger than 500kcmil. Conductors will be THHN copper.
Per table 310.15(B)(16), 4 sets of 500's THHN looks like an option with 2 sets in each of the 2 existing 4" conduits. Using 75C column for 500's is 380A. Each conduit would have 4 CCC (2 sets single phase and 2 neutrals). This would require adjusting at 80% per table 310.15. (380A)(4)(0.80) = 1216A unfortunately not large enough, poco will not allow larger than 500kcmil.
Per table 310.15(B)(16), 6 sets of 350's may work. Per table C.8(A) each 4" PVC conduit will allow the 3 sets (9-350's THHN). Using 3 sets in each conduit, we will have 6 CCC in each conduit. This will require using the 80% adjustment in 310.15 also. (310A)(6)(0.80) = 1488A.
So 6 sets of 350kcmil is adequate considering the 1400A breaker.
Thanks in advance!!!
The project is multifamily. Service load was calculated using 220.84. Load is 1276A with service voltage 240/120V single phase. The meter pack will have a 1400A breaker. The site also has 2 existing 4" schedule 80 pvc conduits. Ideally the 2 existing 4" conduits would be reused and not require trenching. Poco will not allow larger than 500kcmil. Conductors will be THHN copper.
Per table 310.15(B)(16), 4 sets of 500's THHN looks like an option with 2 sets in each of the 2 existing 4" conduits. Using 75C column for 500's is 380A. Each conduit would have 4 CCC (2 sets single phase and 2 neutrals). This would require adjusting at 80% per table 310.15. (380A)(4)(0.80) = 1216A unfortunately not large enough, poco will not allow larger than 500kcmil.
Per table 310.15(B)(16), 6 sets of 350's may work. Per table C.8(A) each 4" PVC conduit will allow the 3 sets (9-350's THHN). Using 3 sets in each conduit, we will have 6 CCC in each conduit. This will require using the 80% adjustment in 310.15 also. (310A)(6)(0.80) = 1488A.
So 6 sets of 350kcmil is adequate considering the 1400A breaker.
Thanks in advance!!!