Single conductor smaller 1/0 on cable tray

Status
Not open for further replies.
Location
miami, FL
Hi, somebody could explain me the technical reason why single conductors smaller 1/0 AWG are not allowed for use on cable trays by NEC 392.10(B)(1)(a)?. Let?s suppose Type TC single conductors smaller than 1/0 are available in commerce.
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
...Let?s suppose Type TC single conductors smaller than 1/0 are available in commerce.
That would certainly be interesting. Art 336.2 defines TC as a factory assembly of two of more insulated conductors ....

Do you have a reference for these 1/c - type TC?

ice
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
Hi, somebody could explain me the technical reason why single conductors smaller 1/0 AWG are not allowed for use on cable trays by NEC 392.10(B)(1)(a)?. ....

I'm not much help. I supect it is an insulation mechanical strength issue. NEC allows grounding conductors down to #4, but not power conductors. No clue how 1/0 was chosen. Possibly another of the Code Panels throwing a blindfolded dart at an ouija board. Believe me, ii's not an easy task - you try getting a dart to hold still while you tie a blindfold on it.

...Let?s suppose Type TC single conductors smaller than 1/0 are available in commerce.
I suspect you meant CT listings. TC is under NEC 336 - entirely different. If so, there are different specs outside of the US. For example Mexico allows use of CT listed single conductors, in cable trays, down to #4. Nope, I don't know how they decided on that either.

ice
 

ron

Senior Member
Single conductor are often referred to as CT rated (Cable tray). An example http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet165

I agree that NEC 392.10(B)(1)(a) limits installations in an industrial environment to 1/0AWG and larger, BUT in a non-industrial environment, like a data center or office space, if you could find CT rated conductors smaller than 1/0AWG, I don't think anyone can stop you.

392.10 only has the limitation for industrial, nothing for other space types.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Ron,
The rule in 392.10(A) limits you to the wiring methods shown in Table 392.10(A) if you are not in an industrial occupancy. 392.10(B) expands that to permit single conductors 1/0 and larger along with the wiring methods in T392.10(A) if you are in an industrial occupancy.
 

ron

Senior Member
Ron,
The rule in 392.10(A) limits you to the wiring methods shown in Table 392.10(A) if you are not in an industrial occupancy. 392.10(B) expands that to permit single conductors 1/0 and larger along with the wiring methods in T392.10(A) if you are in an industrial occupancy.

Thanks, I hadn't looked at it that way before.

FWIW Is there a definition of "power cable" in the code that could be interpreted to mean a single covered conductor rather than a factory assembled group of conductors? The table allows "Other factory-assembled, multiconductor control, signal, or power cables that are specifically approved for installation in cable trays" which a CT conductor would be
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Thanks, I hadn't looked at it that way before.

FWIW Is there a definition of "power cable" in the code that could be interpreted to mean a single covered conductor rather than a factory assembled group of conductors? The table allows "Other factory-assembled, multiconductor control, signal, or power cables that are specifically approved for installation in cable trays" which a CT conductor would be

type W is listed as portable power cable and is available in single conductor. I don't know if it is approved to use in cable tray though.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
One of the issues the code has is the use of the terms "conductors" and "cables". In many cases, but not all, where the code uses "conductor" it means a single conductor and where it uses "cables" it means two or more conductors in an assembly with or without an outer covering.
This should really be addressed in the code as it is a source of confusion.
 
Location
miami, FL
Thanks you guys,
Sorry if I misspelled the letters, I mean CT type single conductor and i did the question because while viewing General Cable?s online catalog (http://www.generalcable.com/generalcable/iCatSearch.html?ic=f0cdd4eb&sc=XHHW-2 CT) I bumped into ref. XHHW-2 CT (page 83) where sizes less than 1/0 are shown while Southwire's table start from 1/0 AWG.

So I just try to figure out why NEC doesn?t allow smaller sizes than 1/0 on cable trays.

But regarding Ron?s comments, if CT type conductor fits Table 392.10(A) as "Other factory-assembled, multiconductor control, signal, or power cables that are specifically approved for installation in cable trays", sizes smaller than 1/0 could be used in a non-industrial environment on cable trays in accordance with NEC?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
But regarding Ron?s comments, if CT type conductor fits Table 392.10(A) as "Other factory-assembled, multiconductor control, signal, or power cables that are specifically approved for installation in cable trays", sizes smaller than 1/0 could be used in a non-industrial environment on cable trays in accordance with NEC?
:thumbsup:
 