Are compression couplings/connectors required on EMT at a fire pump controller? Can I install a set screw connector in a conduit hub and call it a day?
Good question. I'm inclined to think it needs to be a rain-tight compression connector due to 695.6(J)(2) and a fire pump controller enclosure is at least a Type 2 drip-proof.Are compression couplings/connectors required on EMT at a fire pump controller? Can I install a set screw connector in a conduit hub and call it a day?
...hubs only with threaded conduit.
I must be behind the curve on this - where is this written?
It's a big book, Bob.![]()
Fittings with internal female threads (e.g., hubs, conduit bodies, couplings) have only been investigated for use with threaded rigid conduit.
George,I must be behind the curve on this - where is this written?
It would seem that Art. 695 requires something that can't be done within the listing.
Could 695.6(J)(1) also be read as "Where you use a conduit hub, it shall be listed."?
Does it?