This is something different for me. I have a 3 phase Delta-Wye, 30 kVA, 480 ? 208/120 transformer with #10?s ran to the primary and fused at 30 amps.
The way I figure it that works out to technically (potentially) be a 50 amp primary: 30,000 / (480*1.732) * 1.25 = 45.1. But for some reason, someone put in #10?s. So now that?s what I have to work with.
But with the 10?s at the primary, I?m limited to 30 amps; so my question is ; do I use that as my basis for sizing my secondary?
Thus: Determine primary kVA at 30 amps: 480 * 1.732 * 30 = 24.940 kVA
Then size secondary so as not to overload the 30 amp primary: 24.940 / (208 * 1.732) = 69.2
Which would put me at 70 amps.
It makes sense to me to do it this way so as not to overload the primary but I?ve not had the experience before to not size primary and secondary together based on transformer max rating.
The way I figure it that works out to technically (potentially) be a 50 amp primary: 30,000 / (480*1.732) * 1.25 = 45.1. But for some reason, someone put in #10?s. So now that?s what I have to work with.
But with the 10?s at the primary, I?m limited to 30 amps; so my question is ; do I use that as my basis for sizing my secondary?
Thus: Determine primary kVA at 30 amps: 480 * 1.732 * 30 = 24.940 kVA
Then size secondary so as not to overload the 30 amp primary: 24.940 / (208 * 1.732) = 69.2
Which would put me at 70 amps.
It makes sense to me to do it this way so as not to overload the primary but I?ve not had the experience before to not size primary and secondary together based on transformer max rating.