Eddy Current
Senior Member
Does anybody know the code for how many wires you are allowed to put under acorn clamps and water pipe grounding clamps?
One unless you find yourself a special clamp.250.70 Methods of Grounding and Bonding
Conductor Connection to Electrodes
The grounding or bonding conductor shall be connected to
the grounding electrode by exothermic welding, listed lugs,
listed pressure connectors, listed clamps, or other listed
means. Connections depending on solder shall not be used.
Ground clamps shall be listed for the materials of the
grounding electrode and the grounding electrode conductor
and, where used on pipe, rod, or other buried electrodes,
shall also be listed for direct soil burial or concrete encase-
ment. Not more than one conductor shall be connected to the
grounding electrode by a single clamp or fitting unless the
clamp or fitting is listed for multiple conductors. One of the
following methods shall be used:
Does anybody know the code for how many wires you are allowed to put under acorn clamps and water pipe grounding clamps?
One specific section for the application was pointed out. Without that section you still have the listing of the product. A general unwritten rule to remember is that most all conductor termination devices only are designed for one conductor if they are not marked otherwise.
Does anybody know the code for how many wires you are allowed to put under acorn clamps and water pipe grounding clamps?
Why loop and fold and create a violation when you could just go straight through?
NEC only requires the GEC to be unspliced - exception to use irreversible splicing method. GEC is from the service equipment to an electrode. Anything going to an additional electode is a boning jumper and can be spliced without using irreversible methods.Can you put a dual lug into the single lug of the acorn or water pipe clamp?
Not sure of the code article but I'm sure that some grounding methods insist on one continuous cable between supplementary grounds.