The "pool guy" asked me about upping from 120v to 240v for his vfd pool pumps he's installing ( as it was raining on me while I was screwing around with a HP rated switch and a plastic two gang cover).
He's wondering what it would take? Like a ~ 4 or 6 hundred dollar transformer to go from 120 to 240 so he could run this pump and potentially save his costumers hundreds of dollars a year.
Not always playing with the numbers, I sometimes question myself. So am I in the right frame of mind thinking ? That,
Besides the cost of a transformer and wiring,
The motors he is installing are 1.5 HP 10 amp (name plate) So at 240 volt that motor would be on a 20 or 25 amp circuit.
At 120 volt with a transformer, that 120 volt circuit should be 40 or 50 amps.
Is that right?
Thanks