Inspector cited this?
electricg
wa
first time I have seen this cited as a violation. Hope you can see this picture. The faceplate is metal. Inspector says NEC violation with this wall transformer. Guess why.
Obviously because, as is indicated by the position of the label, you have installed the transformer upside down.
Or perhaps that receptacle unit is not UL listed to have anything fastened to it by the center screw except the cover plate?
Your somewhat close, but the transformer being upside down or right side up wasn't the main reason or article he cited, so reading the label has nothing to do with it. I have seen these transformers, (sometimes called wall warts) plugged in like this many of times.
It looks like it will hinder plugging in another plug in the duplex receptacle.
My second guess is the receptacle appears to be slightly recessed in the metal faceplate - it must be flush or extend beyond flush if metal faceplate.
My third guess is securing the transformer under the plate screw interferes with grounding the wall plate.
Solution - snap the tab off the remaining receptacle so that only one is active. The only problem would be if that receptacle was one that was required by Code for that area.
404.9(b) is for switches
406.6(b) is for receptacles
As I was looking for the section Chris had posted the code section.
Does anyone know the Code article that was cited? ;)
Well we have to start with 406.6(B) but it is questionable if bonding is secure enough in this instance so that may send us elsewhere - which I am guessing is what you had there.
110.3(B) is a way out for an inspector that doesn't want to come up with something specific or other logical explanation
I will let you know if I find anything else if it has not been revealed yet.
ETA: maybe something from 250.4 though nothing in there specifically applies to a metal faceplate. I'm guessing you are looking for something fairly general in nature and not specific to the application.