I realize that... but conductive normally non?current-carrying metal parts on the line side of the service disconnecting means are not service entrance and service conductors. There is nothing in the Code which explicitly prohibits parallel grounded conductor current paths on the line side, other than 250.6... and we have no explicit definition of objectionable current.
First, I apologize for using an undefined term "service entrance" when what I meant is embodied by the Article 100 term "Service". To reiterate my point, David, in one illustration of how to control "objectionable current" is altering the connection at the XO of a power company transformer. We don't know yet, from David, whether the transformer low voltage terminals are the "service point", but, regardless, the transformer is not customer owned nor part of a supply that is other than an electric power utility.
The
Code does not permit ONLY current on the grounded service conductor
. The
Code DOES permit multiple current paths between the service main bonding jumper and the service source when the service is supplied by an electric power utility. The
Code permits metallic raceways in the assembly of a "service" supplied by an electric power utility.
That's it. It's that simple. An electric power utility supplied "service" will, by
Code , have current in ALL of the conductive paths present between the service disconnect main bonding jumper and the supply. I submit that, because of
Code requirements for the bonding of conductive enclosures and raceways of a service, current in them is NORMAL.
Thinking of David's metallic raceway between a CT cabinet and a utility transformer cabinet, current in the metal of the raceway, by
Code bonding requirements, is NORMAL. David's raceway is "normally current carrying", and, as such, doesn't meet the description of "
normally non?current-carrying metal parts of equipment" in NEC 250.6(A).
. . . show me where Code permits conductive normally non?current-carrying metal parts to be a parallel conductor for anything other than fault current or surge current from lightning. I'll save you some time and tell you, there is no where in the Code that does... but being considered a permissive text, it does not explicitly prohibit such either. The closest it comes is prohibition of connecting the grounded conductor to the grounding system on the load side of the service disconnecting means.
No problem. Answered above, in this post. I'm not making my point about anything other than the "service" connected to an electric power utility supply.
if I have six conduits each. one 500mcm neutral in each and one 3/0 neutral in each I can take an amp probe and measure the current on each of the 12 conductors.
If I have six conduits each. One 500 MCM neutral in each one 3/0 conductor I now identify with green insulation and move them to the transformer enclosure with a main bonding jumper connecting the XO to the 3/0 conductors in the transformer.
The only thing being excluded is the 3/0 "equipment grounds" no one is excluding the main bonding jumper from the XO to the enclosure no one is excluding the choice of rigid metal conduit.
If I was however the design engineer I would not use metal conduit as a design choice.
David, you are absolutely correct to the technical reduction of current in the rigid metal conduit. I have no trouble understanding this. But, the basis for your request requires rejecting the permissions of the
Code that describe the materials used and electrical assembly of the same into a "service" that is supplied by an electric power utility. In my opinion, excluding
Code permitted service assembly is above the minimum standard of the
Code. If your requirement of applying 250.6(A) stands in your RMC connection to the utility transformer enclosure, then 250.6(A) HAS TO apply to a metallic conduit installed between a 100 Amp 120/240 volt single phase residential service center and the electric power utility meter socket enclosure.