hvac condenser unit. name plate states , 50 amp cb, min. circuit amps. 28. fellow co-worker says #10. I say #6.
thanks for info.
thanks for info.
thanks for info.
thanks for info.
Co-worker wins the bet, 240.3 tells you it is okay.hvac condenser unit. name plate states , 50 amp cb, min. circuit amps. 28. fellow co-worker says #10. I say #6.
thanks for info.
Also with an MCA of 28 amps you could use a 30 amp OCPD.
But although it is acceptable, it may lead to nuisance trips. Mike recommends going to the max allowed OCPD instead.