NEC required Receptacles in an Office Space
Leo1
Los Alamos, NM
What is the Code required minimum number of receptacles in a small office space (approx. 80 SF)?
I plan to install 3, 15AMP, 125VAC, duplex receptacles in the office space. I have talked to the office manager and he has indicated the loads will be 450W for computer and printer, 50W for task lighting and a coffee pot at 950W. So I know 3, 15AMP, duplex receptacles feed from a 20AMP, 120VAC, single pole circuit breaker will provide adequate power. But I am curious if the NEC has a minimum required number of receptacles required in an office space. I have not found a minimum required number of receptacles required.
While there is a minimum calculated load required, there is no minimum number of receptacles required.
As smart mentioned there are almost no required receptacles outside of dwelling units.
One requirement that may apply to you are service receptacles for HVAC equipment. 210.63