SteveBB
- United States
Hello,
I currently am sizing a feeder for a 480VAC 3 phase 3-wire service from a gear to a distribution panel.
600A Bus Panel, No Main Breaker
600A 80% rated OCPD
THHN 90C Wire
Assuming 75C Terminal Ampacity
Here is my approach:
-I believe that with a panel without a main you cannot have an OCPD higher than the bus of the panel, therefore the 600A breaker referred to above.
-Taken that 600A breaker, at 80% limit, panel current will not exceed 480A
-Given the size I am jumping straight to parallel feeder calculations as I'm sure I won't want to deal with single.
6-300kcmil THHN w/ 2-#4 THHN ground in a single 3" rigid conduit
3-250kcmil THHN w/ 1 #4 THHN ground in two parallel 2" rigid conduit (This is the preferable option given to me by the contractor)
To get to the above I:
90C 300kcmil wire is good for 320A * 0.8 for 4-6 conductors in a conduit = 256A which is less than the 75C wire rating of 275A (2 sets for 512A > 480A)
90C 250kcmil wire is good for 290A * 1 for no additional derate = 290A which is more than the 75C wire rating but the 75C rating of 255A still covers the load. (2 sets for 510A > 480A)
Do this seem sound? I've ran it through a calculator I found online and it's telling me I need 350kcmil regardless of single or parallel conduit, so that has me second guessing my calculations. To be more clear, this calculator lists both a "grounded conductor size" and "ungrounded conductor size". The "grounded conductors size" matches my calculations above but the "ungrounded conductor size" is where 350kcmil is listed regardless of single or parallel conduit. This tells me that I am either calculating something wrong or I don't understand what the difference is between a grounded and ungrounded conductor.
600A 80% rated OCPD
THHN 90C Wire