joshtrevino
- Beaumont, TX
I am designing a control room that will be powered by a 120/208v panel. One circuit will power a UPS and UPS distribution panel for computers and lights. The client has requested an isolated ground for the computers tied to a grounding triad. My plan is to specify the UPS panel with two bus bars (one tied to the common building ground and one tied to the grounding triad). I have two questions:
1. My manager says that he thinks the 2011 NEC requires for an "isolated ground" to be tied into the common ground. This does not make sense to me because any noise that you are trying to avoid with an isolated ground would bleed on to your isolated system. Can someone please comment on this with applicable code article?
2. On my branch circuits to the computers am I required to install two grounding wires (one for the conduit/case ground and one for the isolated receptacle ground)? Please comment with article reference.