I am working on a project where there is an industrial control panel with a 600A horizontal bus serving 3 buckets. The original design drawings showed a 100A main fused disconnect bucket but the installed unit is actually only main lugs. It is served off a tap from a wireway from a 480V 3-phase service disconnect with 400A fuses. We need to select the OCPD and add a main disconnect beside the unit. The buckets are as follows:
#1: 100A-3P thermal mag CB serving a 25HP motor and 150VA control transformer.
#2: 100A-3P thermal mag CB serving a 25HP motor and 150VA control transformer.
#3: 50A-2P thermal mag CB serving a 7.5 KVA transformer with a 120/240V sec. this is for a small load center in the bucket. The transformer is actually in the bottom of the control panel which could be considered a 4th bucket.
I am considering this an industrial control panel per the definition even though it looks like a motor control center. Per 409.21.C, I sized it as follows:
100A + 34A (motor #2), + 0.31A (control transformer #1), 0.31A (control transformer #2), 15.6A (7.5KVA/480V for transformer) = 150.22A.
I would select a 150A rated OCPD because NEC 409.21.C says I can't go over the calculated load of 150.22 which means I select the next size down.
Id I calculated it out with the actual panel loads as opposed to the transformer size, I get 147.98A meaning I would need a 125A OCPD (next size down).
This is a struggle because the current OCPD is technically 400A, the bussing is 600A main lug, the original design drawings called for a 100A fused main disconnect bucket, and the panel data tag indicating the amps is blank.
When sizing the OCPD, it seems odd you would add the loads up, and pick the next smaller breaker? Just does niot sound right.
Any advise would be appreciated.