All,
I have a long-time commercial (non-profit) site that I do a lot of work for; both paid and volunteer. The employees there are all very close friends of mine; almost family. They don't have a lot of extra money to burn because they are a non-profit.
They are having a new network/phone system installed. A few weeks ago, I was walking thru the property and saw one of the network contractors with a piece of MC cable and a piece of 10-2 Romex. Thinking that the 10-2 Romex was a bit out of place for a network installation, I asked a few questions and was told that he was a "ex-electrician" and was adding to a circuit for a switch and that he knew what he was doing. I left it go there, but said that I would be checking his work, so it had better be right.
Anyway, I go to check on the work yesterday and found this:

The biggest issue is that the EGC in the MC cable is attached to the receptacle, but NOT to the metal box. I pointed this out to the network guy and he as surprised that this was required. Also, he wanted black receptacles, but rather than buy that color, he spray-painted the face black. Heaven only knows how much paint got on the contacts of the receptacle.
I confronted the contractor about licensing and permits and he gave me a run-around, but couldn't produce either.
Anyway, I think management there listens to me, but second opinions can't hurt to reinforce my point, so if you are willing please answer the poll question and/or provide your opinion.
As always, thanks,
Mark
I have a long-time commercial (non-profit) site that I do a lot of work for; both paid and volunteer. The employees there are all very close friends of mine; almost family. They don't have a lot of extra money to burn because they are a non-profit.
They are having a new network/phone system installed. A few weeks ago, I was walking thru the property and saw one of the network contractors with a piece of MC cable and a piece of 10-2 Romex. Thinking that the 10-2 Romex was a bit out of place for a network installation, I asked a few questions and was told that he was a "ex-electrician" and was adding to a circuit for a switch and that he knew what he was doing. I left it go there, but said that I would be checking his work, so it had better be right.
Anyway, I go to check on the work yesterday and found this:

The biggest issue is that the EGC in the MC cable is attached to the receptacle, but NOT to the metal box. I pointed this out to the network guy and he as surprised that this was required. Also, he wanted black receptacles, but rather than buy that color, he spray-painted the face black. Heaven only knows how much paint got on the contacts of the receptacle.
I confronted the contractor about licensing and permits and he gave me a run-around, but couldn't produce either.
Anyway, I think management there listens to me, but second opinions can't hurt to reinforce my point, so if you are willing please answer the poll question and/or provide your opinion.
As always, thanks,
Mark