Leo1
- Los Alamos, NM
Can a 3/8" diameter stainless steel cable that runs between ski tower poles (approx. 40' high) be considered as the main conductor for lightning protection? Is it UL or the Lighting Protection Institute that would have final say - assuming the local AHJ defers to someone else?
The 3/8" diameter exceeds the cross-section area of 57,400 cir. mils for copper and 98,600 cir. mils for aluminum required by NFPA 780 for the main conductor. Then at each tower install a couple air terminals that bond to the 3/8" stainless cable and a 1/0 CU down conductor to two 3/4" x 10' coppercald ground rods.