back feed

Status
Not open for further replies.

domnic

Senior Member
Occupation
Electrical Contractor
Can i back feed a 60 amp breaker for a disconnect for a sub panel ?
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
Can i back feed a 60 amp breaker for a disconnect for a sub panel ?

see 408.36.D
2008 NEC
Yes, but it must be held in place by an additional fastener that requires other than a pull to release the device from the mounting means on the panel.
 

norcal

Senior Member
see 408.36.D
2008 NEC
Yes, but it must be held in place by an additional fastener that requires other than a pull to release the device from the mounting means on the panel.


Only if it is a plug-in circuit breaker, not required for a bolt-on, but plug-in type is more common.
 
Status
Not open for further replies.
Top