interlock wire colors

Status
Not open for further replies.

rayertz

Member
Location
USA
what are the wire colors for interlocks between separate pieces of equipment?
I.E., Air handler / Condensing unit.

120 vac control power
24 vdc controls
 

xformer

Senior Member
Location
Dallas, Tx
Occupation
Master Electrician
what are the wire colors for interlocks between separate pieces of equipment?
I.E., Air handler / Condensing unit.

120 vac control power
24 vdc controls

Red, black, blue, brown, orange, yellow, white, and green are the most common colors I have seen... :)
 

kwired

Electron manager
Location
NE Nebraska
Different equipment types will often have their own color codes. NEC doesn't regulate this.

For HVAC each color generally has a common function throughout the HVAC industry.

a few are - Red - 24 volt "hot"
White - call for heat
Green - call for indoor blower
Yellow - call for compressor
Orange - reversing valve on heat pumps
Blue - 24 volt "common"

They may have their own standard for color codes of internal wiring but those above are common for field installed controls.
Internal wiring is not subjected to NEC on a listed product so they can and sometimes do use colors the NEC restricts to specific use for other things.
 