xguard
- Baton Rouge, LA
I have a 3 pole 800 AMP circuit breaker disconnect I'd like to tap. I'd like to feed a 100 AMP Circuit breaker disconnect with this tap.
The 800 AMP disconnect has lugs (3 lugs per pole, the other two lugs per pole are for a parallel 600 MCM feeder) that are rated for a minimum 500 MCM conductor. The largest conductor allowed on the 100 AMP Disconnect I'd like to connect this tap to is 1 AWG.
The 500 MCM is as protected as a tap on the 800 A disconnect, if I transition to 1 AWG at the 100 AMP disconnect and the combined length of the 500 MCM and 1 AWG is not more than 10 feet, is this considered a tap from a tap? The combined 10 foot 500MCM/1 AWG section would be protected in accordance with the 1 AWG tap ampacity requirments, 130 AMPS / 800 AMPS greater than 10%.
Thanks for any feedback!