I am paralleling (3)-2MW, 277/480V generators. Due to the low zero sequence impedance, my ground fault current at the paralleling switchgear is way higher than 3-ph fault current. Per my calculation, I have
Three phase fault current: 63,483A (x?d=0.1421) (21,161amp x 3)
Ground fault current: 80,454A (x0=0.0336) (26,818amp x 3)
That being said, I have two questions.
1. Can I just provide 100K AIC CBs (instead of 65K AIC) for higher ground fault current and call it a day? Is 100k AIC CB is rated for 80k ground fault? Isn?t the 100k rating is based on the L-L rating?
2. How about adding a small reactance at the generator so that the ground fault current can be reduced to the 3-ph fault current level? Has anyone done this before? Can it be done by generator mfgrs? Or is this something that has to be done in the field?