Grounding Bushing.
overamped
California
I'm installing a 800 amp 480 volt panel and it's being fed by three parallel runs of 250 MCM with a 1/0 ground in each of the three conduits. Do I need to use grounding bushings on the three conduits inside the breaker panel I am feeding? If so what table do I use to size it and does each conduit get it's own bonding wire?
Check article 250 under bonding.... circuits over 250V :)
So do I need a bonding wire only if I use a concentric knock-out or is it considered a supply side bonding jumper and I either use one wire and size it based on 250-122 or three wires and size it based on 250-66.
Thank you for your reply by the way.
The bonding wire and the supply side Bonding jumper are two different animals...
So do I need a bonding wire only if I use a concentric knock-out or is it considered a supply side bonding jumper and I either use one wire and size it based on 250-122 or three wires and size it based on 250-66.....
Confusing stuff here. SSBJ is for services. Since you said 1/0 ground I'll guess it's an EGC and a feeder.
Quick and dirty rule for bonding jumpers is 250.66 for the Service or SDS and 250.122 for Feeders.
adding one step, and again assuming "ground" in this case means equipment grounding conductor on a feeder ( as opposed to serice grounded conductor),
250.97 will help clarify if a bonding jumper is needed. Unless you encounter concentric/eccentric one is normally not needed.
250.102 should be used for sizing grounded conductors and "bonding" jumpers. Supply side bonding jumpers can be used on services and SDS's. 250.66 is for sizing grounding electrode conductors.
If you use a metallic conduit then you do not need an EGC within each parallel raceway. If you choose to use a wire type EGC then it's sized according to 250.122 and 800 amps, which as you've stated is #1/0. If no concentric or eccentric KO's are encountered then bonding jumpers are not required even at 480 volts. If required they would be #1/0 also.