xformer
- Dallas, Tx
- Master Electrician
How does a disconnect switch disconnect a meter without disconnecting the service...?
How does a disconnect switch disconnect a meter without disconnecting the service...?![]()
I don't know why, but our utility requires that the meter disconnect device have overcurrent protection.It doesn't...230.82(3) permits a disconnecting means for use by the utility for work on their meter. It will disconnect the service, but it won't have any overcurrent protection. The overcurrent protection will be located at or adjacent to the service disconnecting means.
B. Self?Contained Meters
1. Single, and three phase, 480V, less than 201 Amp, services
a) A breaker or fused disconnect located on the line side of the meter (cold sequence metering) is required for all 277/480V and 480V services 200 amp and below.
b) It shall be the customer?s responsibility to provide the proper interrupting rating device on the line side.
c) Ameren should be contacted to determine available short circuit current.
d) Use of separate enclosures for the line side protective device and the meter enclosure is acceptable. However they must be mounted directly above, or on a horizontal plane, within 4 feet of one another.
e) Continuous conduit with no LB?s or any other connector that could allow access to un?metered wiring is allowed between the protective device enclosure and meter enclosure.
f) Sealing provisions for the line side protective device must be provided to prevent access to un?metered conductors within this enclosure.
g) A pad lockable door for access by the customer to operate the protective device should be provided.
Nothing prohibits the meter disconnect from having OCP.I don't know why, but our utility requires that the meter disconnect device have overcurrent protection.
A meter disconnect shall be legibly field marked on its exterior in a manner suitable for the environment as follows:METER DISCONNECT
NOT SERVICE EQUIPMENT