XFMR Disconnect

Status
Not open for further replies.

4fun

Member
Location
Long Valley, NJ
I am hoping someone can help with this question. I have a customer who wants to install a primary disconnect onto an existing pad mounting 480 - 208/120 volt XFMR. They would like to mount it onto the side of the XFMR itself and simply use nipples in and out of the primary compartment. The XFMR is fed with a 3 phase 70 amp breaker located in a remote panelboard. I cannot find where this would be prohibited in the NEC. The alternative would be to breakup the concrete and relocate the conduit.

Any thoughts would be appreciated.
Rich
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I don't see an issue as long as something other than the conduit nipples is used to support the disconnect.
 

Smart $

Esteemed Member
Location
Ohio
While not prohibited by Code, you may run into issues if the intent for the disconnect is to perform servicing where access to the compartment is required. Under a bona fide safety program, the compartment will still have energized conductors when the disconnect is opened, unless the remote breaker is also off... then the opened breaker will have to comply with LOTO. Not impossible, but it leaves me wondering what the intent for the disconnect is.
 

iwire

Moderator
Staff member
Location
Massachusetts
Energized conductors are not an issue are they?

No exposed live parts and we are good to go right?

Just like factory installed disconnects in roof top units and countless other machinery.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Is the proposition to actually bolt the disconnect directly to the transformer or to channel that is mounted to the floor?

I would not have a problem with it bolted to the transformer enclosure as long at the location does not interfere with the access to the connections.
 

Smart $

Esteemed Member
Location
Ohio
Energized conductors are not an issue are they?

No exposed live parts and we are good to go right?

Just like factory installed disconnects in roof top units and countless other machinery.
Possibly, now that you bring it up. What is OSHA's position?

The places I work nowadays require everything above 50V be de-energized related to the piece of equipment to be worked on (when practicable)... otherwise hot PPE. Insulated and touch-safe do not qualify.
 

4fun

Member
Location
Long Valley, NJ
Thanks for the replies. I couldn't find a reason why it would not meet code but I guess I just needed a little reassurance. It will be mounted properly and is just for an easy method of shutting down the equipment.

Sent from my DROID RAZR using Tapatalk
 

rhovee

Member
I would only mount the disconnect in the "buffer" zone. You could get nailed for not following the manufactures installation instructions on the transformer if you go above the line which is usually above the coils.
 