Transportation Guy
- Williamsburg,VA
Good afternoon ladies and gents. I have a project here in VA (2008 NEC) and we are providing a on site Natural Gas generator for fire pump operation ONLY. Per the 2008 Code, if i read 695.4 (1) correctly, it states we have to size the OCPD for locked rotor current. Correct?
In the 2011 cycle, it states in 695.4 (B) (2) size it for instantaneous pickup of the full pump room load (whatever that means) and shall comply with 430.62 which sends me to 430.24, 430.52, or 440.22 (A)
The pump is 40.0 H/P, 3525 RPM,
3 PHASE, 60 CYCLE, 208 VOLT,
The engineer says we need a 700AMP OCPD
The manufacturer says we need only a 400AMP
Help!
Thanks
Help!
Thanks