We are currently wiring a facility that has been classified by the engineer as class 1 div and class 1 div areas.
i have a couple of questions: on the general construction methods of the areas-the walls are 2-layer sheetrock-and the ceiling is an acoustical 2x4 standard everyday lay in tiles.All the electrical is called to be rated for the areas installed-i just have never seen a class 1 div 1 area-with an acoustical ceiling and sheet rock walls.?
We asked the GC how the construction complies-and was told due to the location of the potential gases( height off the floor?)-that above the acoustical ceiling was actually not classified-the areas do have at least 4-air exchanges an hour-minimum
The light fixtures are mounted tight to the ceiling which is about 9' AFG.-does the wiring method above the ceiling need to class 1 div 1 rated.?
There are 2-rooms that are separated by only a sheet rock soffit:-1-ceiling higher than the other-the high ceiling has class 1 div 2 lay in troffer type fixtures-you can walk between both rooms there is no wall separation.
we do not do alot of this type of work-so we are a little confused on how the classifactions were derived.
thank you
thank you