hbendillo
- South carolina
If they insist it is a delta service, it would likely not be ungrounded in my experience. This could be setup as a 480/240 delta with the center of one winding grounded. You would then have a high leg of 416 volts to ground/neutral but that would still be a grounded system. I've in rare cases seen a POCO do this if they have no other option due to having only 2 phases and the neutral available on a Y primary system.
Actually I stated that incorrectly. It is actually an ungrounded open delta service rather than ungrounded delta service as I stated in the beginning. The argument remains the same though. No neutral and no direct ground fault return path back to the source. Not sure what they have available on the primary side. If this is a new primary DIP pole they added for this service I guess they could have provided a single phase primary to save money.