rookie4now
Senior Member

Also, if anyone can recommend a good link for learning more about transformers I'd like to increase my understanding.
Thanks
The copper strap is bonding X0 to the chassis.
Thanks for the input. it is a 480 delta to 480 wye. If I'm understanding this correctly then, we could take the GEC which is currently terminated at the chassis and instead of terminating it there, pull it through the lug on the chassis and terminate it along with the load side neutral to a double lug on the X0. Correct? the load side is a 3P panel with 3 3P 20a circuits for some special equipment that is being installed by others.
Any thought on the building structural steel question?