wallepog
- Hamden, CT
I'm caught between installing that extra grounding electrode and not. Some background: I'm an electrical engineer designing commercial rooftop mounted PV systems. I've watched Mike Holt's video about it and am reluctant to add an extra electrode into the design.
This is for an ungrounded PV system. The racking is all grounded back to the main switchgear. So in short, the racking would be grounded twice; once going back to the switchgear and the other going to the earth.
For Exception No. 1, I've read that the use of "integral with the array" refers to systems where the array and inverter(s) are installed on the same building. Our string-level inverters are indeed located within the array.
It seems this is more of an opinion of what the "load" means. Any opinions or thoughts? Anyone run into this issue with inspectors or other AHJs?
Let me know if additional information about the system is needed.
Thank you!
Thank you!