Neturals in parallel
domnic
Electrical Contractor
I always heard that neutrals in parallel is a BIG NO NO have you ever had a problem with this. what are the dangers of this?
We run parallel neutrals on large services. It is allowed. Large feeders as well.
Are you refering to branch circuit extensions that have grabbed a hot and whatever neutral might be close without consideration that the neutral may be overloaded? Or the hot comes from LP 3 but the neutral connects to LP 4? Or...
That would be more often described as crossed neutrals rather than parallel neutrals.
There can also be problems if neutrals from different branches are put under one wire nut at an intermediate box.
Let?s clarify the language here. Two conductors are in parallel if, and only if, they are joined at both ends. As ptonsparky mentioned, you can use parallel conductors to increase the ampacity of feeders and services. 310.10(H) has the applicable rules. One of the rules would prohibit paralleling the neutral (or ungrounded) conductors for most of the branch circuits we commonly deal with. The minimum size for paralleling conductors is 1/0, and most of my branch circuits use #12 or #10.
Different from this situation is using a single neutral wire to serve as the return path for more than one branch circuit. I think this is what ptonsparky and GoldDigger described. That is allowed only under very specific conditions that are described in 210.4. If the two branch circuits originate from different phases of the same panelboard, and if their breakers have listed handle ties (or are multiple-pole breakers), then perhaps this creates a legal ?multi-wire branch circuit.? If the two branch circuits originate from the same phase, or originate from different panelboards, or do not have common trip capability, then this is illegal and unsafe.
Now, having said all that, please tell me whether you are talking about a parallel situation, or about a MWBC situation, or about something else.
Are you talking about smaller conductor for 15 and 20 amp branch circuits? In other words the idea of the neutral going back in two different paths back to the panel?
Neturals in paralle
Neturals in paralle
I was talking about objectionable current in the conduit.