Working on a project at a remote location where power will be generated by onsite parallel units operating at 480V 3-phase. The power generators will be connected to a common switchboard bus then the switchboard main disconnect will be the feed out to the main distribution panel. My plan was to have the neutral to ground bond occur in the switchboard and the ground rods bond here at the switchboard. The power generators will not have a neutral-ground bond. No ground rods at the generators and separate ground and neutral wires will be ran between the switchboard and generators. I am looking for NEC references to back this up as I am having a hard time grasping not treating them like a utility as in having each power generator grounded with rods, a N-G bod at the alternators, and a single "grounded" conductor ran from each unit to the switchboard then having them main N-G bond. There is no GFI requirements. If the utility was involved and there was a transfer switch, then NEC 250.11 and 250.12 would make this clearer, but no utility.