If you assume a perfect ground at the POCO secondary and .02 ohms in the grounded conductor from your service bond point to the secondary (corresponding to 2V drop when pulling an unbalanced 100A), then the current in your GEC should be about 8ma by my calculations.
As Mark said - depends on the voltage drop of the normal current path. The more load you have flowing on that normal path the more voltage drop there will be as well.At 8 mA if i disconnect the egc at the ground rod and touch the egc in one hand and the ground rod in the other will i feel a shock?
I just figured that would be a reasonable single-wire voltage drop to shoot for on the service side. That would correspond to a 4 volt drop on a 120V 100A load, which would be ~3%.HOW did you figure the 2 volt drop?