LRB
- Interior Alaska
I would like to run TC-ER to several motors in Class II Div2 area, however, Art 502 does not recognize TC-ER as a means for Flexible connection or as a recognized wiring method for Class II Div 2. Am I correct in my interpretation? The only wiring method I see approved for direct run from cable tray to utilization equipment is interlocked armor Type MC with polymeric jacket and fittings approved for Class II Div 1. I could use TC-ER but would have to protect it with Liquidtight and listed fittings when leaving cable tray (max 6 ft unsupported). Also 502.30(B) would require me to run a bonding jumper around the Liquidtight (2011). My supplier has suggested CLX Cable which I believe meets the interlocked armor Type MC requirement. Any other suggestions welcome.