During a hotel renovation we have discovered that each room has it's own panel each with a 40 amp breaker back feeding and acting as a main. The feeders (#6 copper) come from junction boxes in the corridors. Each junction boxes services 3 rooms and these are also fed with #6 copper conductors on a 60 amp breaker in a "main" panel.
So you have #6 copper conductors on a 60 amp breaker feeding a junction box. From the junction box is 3 sets of #6 copper feeding 3-40 amp panels. Are these conductors large enough? The farthest junction box from the main panel is 200 feet.
These wires are run in 1" EMT with no separate ground wire. Two hots and a neutral with the EMT acting as a ground. The ground bars are bonded to the panels and the neutral bar are not. There are no grounding bushings.
Should there be a separate ground wire as far as codes goes?