jbishop
- hudson, mi
I don't have alot of expeirience with transformers so i'm sure you guys can help me out here.
Here is the issue, we are upgrading some lighting in a factory and when working in one of the panels I noticed that the cabinet was 120v to neutral. With further investigation I found that there was a scraped # 12 THHN in an LB that was cuasing the cabinet to be hot. I also checked from the main service cabinet to the neutral in the panel I found the issue in and had the same 120v. Its a 480 3 phase service the panel with the issue was fed from a transformer that dropped the voltage down to 120/240 single phase. They have 2 other similar transformers in the building neither one of these have the same issue. We replaced the transformer and everything is fine now. My question is how can we send 120v to ground without tripping a 20 amp breaker? And how do you test for this problem? I put a megger from the transformer enclosure to each winding and the lowest reading I got was 10 G-Ohms.
Thanks
Thanks