Fronius 550 Status Code
hossak8
NY
One of four 10.0-3 inverters showed a blinking green and Code 550, and was producing about 25% less than the others. These are fed by 4 strings of 11 Renesola 300's with an Isc of 8.69, and there are 15A fuses in all four strings. All inverters have Delta lightning arrestors.
I shut down the inverter, removed all fuses, and switched the jumper to smoff (the jumper was correctly in smon initially), the fuse in string 2 was blown, and string 2 was showing zero voltage at the input terminals (with wires from the array connected)...all other strings were showing voltage correct for the conditions. The fuses are mounted on a circuit board.
While checking the array for mechanical/connection issues, I noticed over 300 ohms on string 2. Returning to the inverters, I disconnected string 2 from the inverter terminals, and got similar ohms checking from string 2 + to - DC terminals.
I reconnected string 2 at the array, and now got voltage that corresponded with the other strings at the inverter with the string 2 wires disconnected from the DC inverter terminals.
I don't want to use these terminals again, and will move string 2 to an unused input with a new fuse. Any suggestions / feedback would be appreciated.
Sound like lightning damage? We've had some storms since I was last at the site.
An inverter with code 449 turned out to have an unplugged ribbon cable between the power modules in the upper section due to shipping damage (loose filter pulling on cables - shipping damage).