SceneryDriver
- NJ
- Electrical and Automation Designer
Hi All,
My company is moving into a new shop building, and as we've been setting up, we discovered the EC did something strange with the receptacles meant for our MIG and TIG welders. I'm fairly certain I've identified the code violation(s) that we can hang our hats on in order to request a fix, but I wanted to run it by the brain trust here.
Here's the situation:
(3) separate shop areas; Metalworking, Assembly/Carpentry, and Machine Shop.
In the Metalworking area:
(6) 6-50 straight-blade receptacles, all on (1) 80A 2-pole breaker #4 CU THWN supply conductors, #6 taps at the receptacle, splices with split bolts and tape.
In the Assembly/Carpentry area:
(7) 6-50 straight-blade receptacles, all on (1) 50A 2-pole breaker. Unsure on supply conductor size; I haven't been in those boxes yet.
In the Machine Shop:
(6) 6-50 straight-blade receptacles, all on (1) 50A 2-pole breaker. Unsure on supply conductor size; I haven't been in those boxes yet.
Code violations I believe I've identified (assume 2011 code)
-630.11(B) Minimum conductor ampacity shall
be based on the individual currents determined in 630.11(A)
as the sum of 100 percent of the two largest welders, plus
85 percent of the third largest welder, plus 70 percent of the
fourth largest welder, plus 60 percent of all remaining welders.
Even in the Metalworking Area, which is fed from an 80A breaker, we can easily find ourselves operating (4) welders at a time. Based on the draw of our welders, and the math in 630.11(B), we exceed the ampacity of the supply conductors for the circuit (#4 CU, THWN). That said, we'd trip the 80A breaker as well.
-Table 210.21(B)(3) Receptacle Ratings for Various Size Circuits
At least in the Metalworking area, the receptacles, rated for 50A, are fed from an 80A circuit.
I believe the j-boxes with the split-bolt splices are over-filled; I had a devil of a time getting the receptacle I pulled for inspection back into the box. I will do the wire fill math tomorrow and get back to the thread. Incidentally, how does one account for the considerable bilk of split bolts and tape when doing wire fill calcs?
I know the NEC isn't a design guide, and you can do dumb things that aren't a violation, but these welder outlets seem to be a screw-up on the part of the EC. Especially in the Metalworking area, where they're fed from an 80A breaker. Please let me know if I've missed a code violation, or if I'm off in the weeds. We'd like to try to find a violation or two to strengthen our case with the EC that it's their problem to fix, not ours.
Thanks!
SceneryDriver
edit: formatting
| Circuit Rating (Amperes) | Receptacle Rating (Amperes) |
| 15 | Not over 15 |
| 20 | 15 or 20 |
| 30 | 30 |
| 40 | 40 or 50 |
| 50 | 50 |
Thanks!
SceneryDriver
edit: formatting