JustWork
Member
- Location
- New Jersey
Hello We have been performing installs in a manner that was allowed to have the meter socket lugs, main/service disconnect breaker lugs to be at the BFE +1 height and the enclosure in which they are in may be below the BFE+1 height. Like others here I assume :happy no: we have performed many service installs since the Sandy storm at the Jersey shore with so many different added requirements from local authorities and the utility companies that service the areas. We were required to maintain all service equipment including the meter sockets to be at BFE+1 some of the installs would put the meters above the utilities required 60" height which passed with local inspection as well as the utility company. Not to long ago the utility company started enforcing the requirement to maintain this 60" to the center of meter socket which has now caused some issues for us not passing our electrical inspections and having to deal with this new issue of the equipment being below the BFE. In most cases it does get approved but it ends up going back and forth. Enough of the long winded rant where in black and white does it give actual wording that the electrical enclosure/equipment/device must be above BFE+1 FEMA, . Icc or IBCI do understand Article 682 states that no electrical equipment or their enclosures can be below the electrical datum. Does this issue fall under this requirement?:? I do apologize if this topic was already discussed.