mshields
 - Boston, MA
I've designed a system consisting of a 125kW, 208Y/120V diesel generator in skin tight enclosure, belly tank and with a single OCPD (sized at 125% of FLA).  I go underground and up into the main electrical room (RI Code allows for my Emergency System to be in the same room because it's less than 150V to ground).  Directly above where I come from underground into this room I have a wireway off of which are:
1. My emergency OCPD
2. My Standby power OCPD
I utilize MI cable from the Emergency OCPD to the Emergency panel which is in the same room.
An inspector reviewing my drawings, had this to say:
"The OCD at the Generator (450 A) is in front of the two OCD's for the Emergency and Standby circuits are not in conformance with NEC article 700.10, ( if this OCD is eliminated the conductors to the building would be subject to NEC article 445.13 )"
He seems to be saying that if I eliminate the first OCPD at the generator, I'd be ok so long as my conductors are 115% in keeping with 445.13. Bearing in mind that this OCPD (at the generator) coordinates to .01 with the Emergency OCPD at the wireway as well as with Emergency panelboard breakers, I think my design is NEC 2014 code compliant. What do you think?