rwilsond
- Orange County, CA 19 years of exp.
My General Contractor promised me a quality code-compliant installation. But they seem to me to be better at carpentry and plumbing, than electrical. This installation consists of three Type NM, #14/2 AWG cables "sleeved" in Flexible Metallic Conduit (FMC) for protection from damage. These cables leave the wall, and enter kitchen cabinets for connection to receptacles for the under-counter items (Garbage Disposer & Dishwasher), and the receptacles that serve the counter-top). They're telling me that this installation is perfectly code-compliant, and I should be happy with it. However, I believe this installation has the following issues at a minimum:
1) No more than one of these cables can enter into a 1/2" FMC (due to cross-section and heating considerations). Thus, another FMC must be added, and one of the cables transferred to it.
2) A bushing is required at the taped ends of the FMCs.
3) The ends of the FMCs must be inserted into the wall.
4) Each FMC must be secured within 12" of entering the cabinet.
Additionally, I would like to tell them that the cables and FMCs must all be terminated into/onto one or more electrical boxes on or within the wall, with adequate fittings, but I am unable to find such a requirement within the NEC.
Please tell me if any of my NEC interpretations are off-base, and of anything that I missed.